0 members (), 1,355 guests, and 9 robots.
List all of the sections in the 2002 NEC that cover the requirements for removal of abandoned wiring.
372.13 Discontinued Outlets.
When an outlet is abandoned, discontinued, or removed, the sections of circuit conductors supplying the outlet shall be removed from the raceway. No splices or reinsulated conductors, such as would be the case of abandoned outlets on loop wiring, shall be allowed in raceways.
374.7 Discontinued Outlets.
When an outlet is abandoned, discontinued, or removed, the sections of circuit conductors supplying the outlet shall be removed from the raceway. No splices or reinsulated conductors, such as would be the case with abandoned outlets on loop wiring, shall be allowed in raceways.
390.7 Discontinued Outlets.
640.2 Definitions.
For purposes of this article, the following definitions apply.
Abandoned Audio Distribution Cable. Installed audio distribution cable that is not terminated at equipment and not identified for future use with a tag.
640.3 Locations and Other Articles.
Circuits and equipment shall comply with 640.3(A) through (L), as applicable.
(A) Spread of Fire or Products of Combustion. The accessible portion of abandoned audio distribution cables shall not be permitted to remain. See 300.21.
645.5(D)(6) Abandoned cables shall not be permitted to remain unless contained in metal raceways.
725.2 Definitions.
Abandoned Class 2, Class 3, and PLTC Cable. Installed Class 2, Class 3, and PLTC cable that is not terminated at equipment and not identified for future use with a tag.
725.3 Locations and Other Articles.
Circuits and equipment shall comply with the articles or sections listed in 725.3(A) through (E). Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.
(A) Number and Size of Conductors in Raceway. Section 300.17.
(B) Spread of Fire or Products of Combustion. Section 300.21. The accessible portion of abandoned Class 2, Class 3, and PLTC cables shall not be permitted to remain.
(C) Ducts, Plenums, and Other Air-Handling Spaces. Section 300.22 for Class 1, Class 2, and Class 3 circuits installed in ducts, plenums, or other space used for environmental air. Type CL2P or CL3P cables shall be permitted for Class 2 and Class 3 circuits.
725.61 Applications of Listed Class 2, Class 3, and PLTC Cables.
Class 2, Class 3, and PLTC cables shall comply with any of the requirements described in 725.61(A) through (F).
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CL2P or CL3P. Abandoned cables shall not be permitted to remain. Listed wires and cables installed in compliance with 300.22 shall be permitted.
(B) Riser. Cables installed in risers shall be as described in any of (1), (2), or (3):
(1) Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type CL2R or CL3R. Floor penetrations requiring Type CL2R or CL3R shall contain only cables suitable for riser or plenum use. Abandoned cables shall not be permitted to remain.
(2) Other cables as covered in Table 725.61 and other listed wiring methods as covered in Chapter 3 shall be installed in metal raceways or located in a fireproof shaft having firestops at each floor.
(3) Type CL2, CL3, CL2X, and CL3X cables shall be permitted in one- and two-family dwellings.
FPN: See 300.21 for firestop requirements for floor penetrations.
725.61(E) Other Wiring Within Buildings. Cables installed in building locations other than those covered in 725.61(A) through (D) shall be as described in any of (1) through (6). Abandoned cables in hollow spaces shall not be permitted to remain.
760.2 Definitions.
Abandoned Fire Alarm Cable. Installed fire alarm cable that is not terminated at equipment other than a connector and not identified for future use with a tag.
760.3 Locations and Other Articles.
Circuits and equipment shall comply with 760.3(A) through (F). Only those sections of Article 300 referenced in this article shall apply to fire alarm systems.
(A) Spread of Fire or Products of Combustion. Section 300.21. The accessible portion of abandoned fire alarm cables shall not be permitted to remain.
760.61 Applications of Listed PLFA Cables.
PLFA cables shall comply with the requirements described in either 760.61(A), (B), or (C) or where cable substitutions are made as shown in 760.61(D).
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type FPLP. Abandoned cables shall not be permitted to remain. Types FPLP, FPLR, and FPL cables installed in compliance with 300.22 shall be permitted.
(B) Riser. Cables installed in risers shall be as described in either (1), (2), or (3):
(1) Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type FPLR. Floor penetrations requiring Type FPLR shall contain only cables suitable for riser or plenum use. Abandoned cables shall not be permitted to remain.
(2) Other cables shall be installed in metal raceways or located in a fireproof shaft having firestops at each floor.
(3) Type FPL cable shall be permitted in one- and two-family dwellings.
770.2 Definitions.
Abandoned Optical Fiber Cable. Installed optical fiber cable that is not terminated at equipment other than a connector and not identified for future use with a tag.
770.3 Locations and Other Articles.
Circuits and equipment shall comply with 770.3(A) and (B). Only those sections of Article 300 referenced in this article shall apply to optical fiber cables and raceways.
(A) Spread of Fire or Products of Combustion. The requirements of 300.21 for electrical installations shall also apply to installations of optical fiber cables and raceways. The accessible portion of abandoned optical fiber cables shall not be permitted to remain.
770.53 Applications of Listed Optical Fiber Cables and Raceways.
Nonconductive and conductive optical fiber cables shall comply with any of the requirements given in 770.53(A) through (E) or where cable substitutions are made as shown in 770.53(F).
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type OFNP or OFCP. Abandoned cables shall not be permitted to remain. Types OFNR, OFCR, OFNG, OFN, OFCG, and OFC cables installed in compliance with 300.22 shall be permitted. Listed plenum optical fiber raceways shall be permitted to be installed in ducts and plenums as described in 300.22(B) and in other spaces used for environmental air as described in 300.22(C). Only types OFNP and OFCP cables shall be permitted to be installed in these raceways.
(B) Riser. Cables installed in risers shall be as described in any of the following:
(1) Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type OFNR or OFCR. Floor penetrations requiring Type OFNR or OFCR shall contain only cables suitable for riser or plenum use. Abandoned cables shall not be permitted to remain. Listed riser optical fiber raceways shall be permitted to be installed in vertical riser runs in a shaft from floor to floor. Only Types OFNP, OFCP, OFNR and OFCR cables shall be permitted to be installed in these raceways.
(2) Types OFNG, OFN, OFCG, and OFC cables shall be permitted to be encased in a metal raceway or located in a fireproof shaft having firestops at each floor.
(3) Types OFNG, OFN, OFCG, and OFC cables shall be permitted in one- and two-family dwellings.
800.2 Definitions.
See Article 100. For purposes of this article, the following additional definitions apply.
Abandoned Communications Cable. Installed communications cable that is not terminated at both ends at a connector or other equipment and not identified for future use with a tag.
800.52(B) Spread of Fire or Products of Combustion. Installations in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion is not substantially increased. Openings around penetrations through fire resistance-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.
The accessible portion of abandonedcommunications cables shall not be permitted to remain.
FPN: Directories of electrical construction materials published by qualified testing laboratories contain many listing installation restrictions necessary to maintain the fire-resistive rating of assemblies where penetrations or openings are made.
800.53 Applications of Listed Communications Wires and Cables and Communications Raceways.
Communications wires and cables shall comply with the requirements of 800.53(A) through (F) or where cable substitutions are made in accordance with 800.53(G).
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CMP. Abandoned cables shall not be permitted to remain. Types CMP, CMR, CMG, CM, and CMX and communications wire installed in compliance with 300.22 shall be permitted. Listed plenum communications raceways shall be permitted to be installed in ducts and plenums as described in 300.22(B) and in other spaces used for environmental air as described in 300.22(C). Only Type CMP cable shall be permitted to be installed in these raceways.
(B) Riser. Cables installed in risers shall comply with 800.53(B)(1), (B)(2), or (B)(3).
(1) Cables in Vertical Runs. Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type CMR. Floor penetrations requiring Type CMR shall contain only cables suitable for riser or plenum use. Abandoned cables shall not be permitted to remain. Listed riser communications raceways shall be permitted to be installed in vertical riser runs in a shaft from floor to floor. Only Type CMR and CMP cables shall be permitted to be installed in these raceways.
(2) Metal Raceways or Fireproof Shafts. Listed communications cables shall be encased in a metal raceway or located in a fireproof shaft having firestops at each floor.
(3) One- and Two-Family Dwellings. Type CM and CMX cable shall be permitted in one- and two-family dwellings.
FPN: See 800.52(B) for firestop requirements for floor penetrations.
820.2 Definitions.
See Article 100. For the purposes of this article, the following additional definitions apply.
Abandoned Coaxial Cable. Installed coaxial cable that is not terminated at equipment other than a coaxial connector and not identified for future use with a tag.
820.2 Definitions.
820.3 Locations and Other Articles.
Circuits and equipment shall comply with 820.3(A) through (G).
(A) Spread of Fire or Products of Combustion. Section 300.21 shall apply. The accessible portion of Abandoned coaxial cables shall not be permitted to remain.
820.53 Applications of Listed CATV Cables.
CATV cables shall comply with the requirements of 820.53(A) through (D) or where cable substitutions are made as shown in Table 820.53.
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CATVP. Abandoned cables shall not be permitted to remain. Types CATVP, CATVR, CATV, and CATVX cables installed in compliance with 300.22 shall be permitted.
(B) Riser. Cables installed in risers shall comply with any of the requirements of 820.53(B)(1) through (B)(3).
(1) Cables in Vertical Runs. Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type CATVR. Floor penetrations requiring Type CATVR shall contain only cables suitable for riser or plenum use. AbandonedAbandoned cables shall not be permitted to remain.
(2) Metal Raceways or Fireproof Shafts. Types CATV and CATVX cables shall be permitted to be encased in a metal raceway or located in a fireproof shaft having firestops at each floor.
(3) One- and Two-Family Dwellings. Types CATV and CATVX cables shall be permitted in one- and two-family dwellings.
FPN: See 820.53(A) for the firestop requirements for floor penetrations.
(C) Cable Trays. Cables installed in cable trays shall be Types CATVP, CATVR, and CATV.
(D) Other Wiring Within Buildings. Cables installed in building locations other than the locations covered in 820.53(A) and (B) shall be with any of the requirements in 820.53(D)(1) through (5). Abandoned cables in hollow spaces shall not be permitted to remain.
(1) General. Type CATV shall be permitted.
(2) In Raceways. Type CATVX shall be permitted to be installed in a raceway.
(3) Nonconcealed Spaces. Type CATVX shall be permitted to be installed in nonconcealed spaces where the exposed length of cable does not exceed 3 m (10 ft).
830.2 Definitions.
Abandoned Network-Powered Broadband Communications Cable. Installed network-powered broadband communications cable that is not terminated at equipment other than a connector and not identified for future use with a tag.
830.3 Locations and Other Articles.
Circuits and equipment shall comply with 830.3(A) through (D).
(A) Spread of Fire or Products of Combustion. Section 300.21 shall apply. The accessible portion of abandoned network-powered broadband communications cables shall not be permitted to remain.
830.55 Low-Power Network-Powered Broadband Communications System Wiring Methods.
Low-power network-powered broadband communications systems shall comply with any of the requirements of 830.55(A) through (D).
(A) In Buildings. Low-power network-powered broadband communications systems shall be installed within buildings using listed Type BLX or Type BLP network-powered broadband communications low power cables.
(B) Ducts, Plenums, and Other Air-Handling Spaces. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type BLP. Abandoned cables shall not be permitted to remain. Type BLX cable installed in compliance with 300.22 shall be permitted.
(C) Riser. Cables installed in risers shall comply with any of the requirements in 830.55(C)(1), (C)(2), or (C)(3).
(1) Cables in Vertical Runs. Cables installed in vertical runs and penetrating more than one floor, or cables installed in vertical runs in a shaft, shall be Type BLP or BMR. Floor penetrations requiring Type BMR shall contain only cables suitable for riser or plenum use. Abandoned cables shall not be permitted to remain.
Joe,
What makes an outlet 'abandoned, discontinued, or removed' ?
Bill:
First, the subject of "Discontinued Outlets" is only mentioned in Cellular Concrete Floor Raceways; Cellular Metal Floor Raceways; and Underfloor Raceways.
Abandoned: http://www.dictionary.com/search?q=abandoned
I tried to get the following rule added to the NEC in Article 110 and it was shot down:
"Permanent wiring abandoned in place shall be tagged or otherwise identified at its termination and junction points as “Abandoned in Place” or removed from all accessible areas and insulated from contact with other live electrical wiring or devices."
In NFPA 75, this statement is really why we have to pay attention to the removal requirements mentioned here: "Abandoned cable can interfere with airflow and extinguishing systems. Abandoned cable also adds to the fuel loading.
Joe,
Here is another good one. As everyone says, How do you know if it is abandoned? I try to enforce this one and most times I can get most of the old wiring removed. The contractors don't want to spend days and days, tracing out old wire. If the see that it is easily disconnected, then they will usually remove it. There is another good one in the NEC like this. How about "In a workman like manner.." That rule is hard to prove or enforce. ( I feel.)
Harold
O
How about 300.11(c)
GreatIdea!
What's "loop wiring".. as in the UK?
Joe, I'm all for the removal of useless/potentially dangerous wiring, and always agreed with the LA Code providing for such...but there's not much below the 600+ areas of the Code to provide for the removal of this crap. Seems like all they can see is the LV, data, phone, etc.
I had my foremen mark cover plates on "customer future" J/B's with a Scull&Crossbones, and mark it "Customer Death Box"
Yeah, I'm pretty sick, but my heart's in the right place [Linked Image]
From the 2002 NECH:
