ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Meter vs Bricklayer
Meter vs Bricklayer

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 318 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101307 03/04/07 07:37 PM
Joined: Jan 2007
Posts: 59
D
Member
As I said in an earlier post a while ago,we are slow at work right now so me and my buddy find ourselves going on other peoples jobs.I am about finished hot-checking this house now on Pensecola Beach where among other things,the sub feed to the panel upstairs is 2 conductor and grond to main lug panel on breaker in service downstairs....Anyone see a problem here?

Horizontal Ad
#101308 03/04/07 09:51 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I don't see a problem with it as long as the wires are protected at their ampacity and all they need is single voltage circuits. Hopefully one of the insulated conductors is the "grounded" conductor and one is the "grounding" conductor. I see that combination sometimes when a contractor has to refeed an existing subpanel after relocating the Service to accomodate a room addition. If they can't get to the existing panel with SER they wil use the existing SE cable and convert the old panel to 120v. This means connecting both bus to the same side of the line. Kinda hookey and maybe wouldn't pass for new construction but it's safe IMHO. It does potentially put the system in an unbalanced state but one could compensate for this at the main service.


George Little
#101309 03/04/07 09:54 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Sounds like your down there in gfretwell area of the country so I'm sure he'll have something to add to this issue.


George Little
#101310 03/05/07 10:53 AM
Joined: Sep 2003
Posts: 650
W
Member
George described the _right_ way to do this. If you have 2 insulated conductor and a grounding conductor, then you can feed a 120V subpanel. This means one insulated 'hot' conductor, one insulated 'grounded' conductor, and one bare equipment grounding conductor.

Just to make it very explicit: if this is a 120/240V panel, where the bare conductor is being used as the grounded current carrying conductor, then you have clear violations of code.

-Jon

#101311 03/05/07 07:20 PM
Joined: Jan 2007
Posts: 59
D
Member
Yeah,Ikindo posted this to bore you:}It is 120-240 but I thought I would get some of you guys input...I don't wanna start anything but I wonder where the line is drawn sometimes.I would have defintly changed it...I also wonder if my bosses ever had it drawn to their attention.I guess I will MODESTLY mention it

#101312 03/05/07 09:45 PM
Joined: Nov 2002
Posts: 793
Likes: 3
W
Member
Quote
If they can't get to the existing panel with SER they wil use the existing SE cable and convert the old panel to 120v. This means connecting both bus to the same side of the line.

This gets a little problem if there are any shared neutrals between circuits.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
Popular Topics(Views)
352,465 Are you busy
276,132 Re: Forum
255,638 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5