0 members (), 1,212 guests, and 10 robots.
#100136 10/24/06 10:03 PM
Y
But it MUST be a Listed and labled Unit if it is Not then Disconnect must be required to comply with 695.4 (B) 1 & 2 .
Work Gear for Electricians and the Trades
Workgear for Electricians
#100137 10/25/06 09:54 AM
I'm not saying no way to a Listed unit. My question is, IS it a Listed unit?.
"This construction does comply with NFPA-20, UL-218 and FM-1321/1323"
I'm always suspicious (even of myself!). "Does comply" could be weasel-wording for "we designed it to meet the requirements of the standard. It was never submitted to an NRTL for certification, but in our opinion it does comply".
I've seen this a gazillion times in telecom. NEBS testing, to meet baby bell's network safety and reliability testing, cost around $100,000 for a complete set of tests on a typical product. Consequently, in marketing literature the words "meets NEBS requirement" and "designed for NEBS" are more common than "NEBS certified". Why spend a hundred grand when you can just use a misleading phrase instead?
#100138 10/28/06 10:07 PM
Electech
I agree with what you are saying. The wording "complies with" is not the same as being UL Listed.
Look for the listing and go to the online White Book/Orange Book to see if this unit is in fact UL Listed as suitable.
Pierre Belarge