0 members (), 1,190 guests, and 15 robots.
#100051 10/07/06 10:08 PM
Can I make up my own extension cord for use on the job? Look at 240.5(B)(3).
George Little
Workgear for Electricians
#100052 10/07/06 10:39 PM
Sure, the NEC doesn't apply to cords that you are using on your job site. It is an installation standard. [90.2(A)]
Ryan Jackson,
Salt Lake City
#100053 10/07/06 10:54 PM
Your right Ryan. For some reason I was remembering the section that used the words "Listed cord sets" and when I did find it, it was "Listed GFCI protection". Must be the CRS kicking in again.
George Little
#100054 10/07/06 11:32 PM
OSHA rules may apply.
#100055 10/19/06 11:28 AM
OSHA 1926 subpart K would apply, The wire would need to be 12AWG and the connectors on the ends would need to be rated for use in that application.
The practice of making up a 2g box on the end would be unacceptable.
Bryan L. Key
Safety Inspector/Trainer
Terry's Electric Inc.
An Xcelecom Company
600 N. Thacker Ave., Suite A
Kissimmee, Florida 34741
#100056 10/19/06 02:11 PM
BKey, I believe the # 12 minimum is the smallest cord that is allowed to be repaired, I don't think it pertains to making a cord.
If it does can you post the exact section?
Roger