Guys
Sounds good but can't be done. Why As I Stated before '
#1 Generator has Several breakers at it one feeds Fire Pump Transfer Switch other feeds 4 pole to Bld loads. SO Generator MUST be bonded at ist Breaker.
#2
Fire Pump transfer switch is Fed from the NORMAL power source straight from the transformer THUS MUST be bonded at ist disconect(Transfer switch).
So again Three Phases and a Equipment Gr. comes from Generator is Right.
So in Firepump transfer switch you have From Generator 3 phases and Equipment gr.
From Service 3 phases and Neutral. I feel there NO Way with this set up it can be hooked up to code the way its set up.