My ispection was failed because the inspector said all multiwire branch circuit that share a neutral must be on a tied breaker.

In my situation i had two single breakers on two different busbars feeding two receptacles for garebage disposer and the washing machine.

My understanding is whenever there is a peotential difference between the ungrounded conductors on one device then the breaker has to be tied.

Is he correct in his statement?

Thanks