Where you bond the neutral and where you land the ground electrode conductor are two separate things. You can attach the ground electrode conductor anywhere from the service point to the service disconnect but the neutral should onl;y get bonded in the service disconnect. Also you can tap in supplimentry electrode conductors and the GEC to each disconnect. In reality only the biggest one needs to be unspliced.