Min cir- 30.2
Max fuse - 35
I am sure I have to checge the disconnect. But can I get by with the 35 amp allowance for #10 for HVAC loads.
Does *240.4(D)> 240.4(G)table ( Air-condition refrigeration) > 440,part VI allow the # 10 to be protected at 35 amps ?
I am confused to say the least.
Seems like one day after 20 years I maybe can actually fuse # 10 at 35 amps as per 310-16. If not why do they even list 35 amps for #10