As long as the OCPD at the disconenct protects each panel at or below its rated ampacity, I see no problem with this. You just can't use a 400 amp OCPD to supply 2 200 amp MLO panels. You would have to use a 200 amp OCPD to supply the 2 200 amp MLO panels. Don(rsqcapt19)