If this is the neutral bar in the service disconnect enclosure where the MBJ lives I don't see a parallel neutral problem. You can parallel all the grounding conductors you like, code wise. You do it every day when you pull a hard ground in a steel raceway. If that gets supported by building steel you grounded it to the electrode again.
There may be eddy currents but no parallel circuit current.
That is the rational for IG.


Greg Fretwell