Aren't GFCIs "controllers" (switches)?

Also the instructions require regular testing.

We do not install the GFCIs for whirlpools under the tub, we install 'faceless' ones in the wall beside the tub.

[Linked Image from growtron.com]

Quote
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.



[This message has been edited by iwire (edited 12-02-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts