I do not believe there is a need for a specific exception for ranges.

A 50 amp single receptacle can be supplied with a 30 amp branch circuit.

A 100 amp single receptacle can be supplied with a 30 amp branch circuit.

This is the rule for single receptacles.

Quote
220.21(B)(10 Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

Bob

[This message has been edited by iwire (edited 11-15-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts