The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.
Not if the circuit supplies a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
See 240.4(B)(1).
Don


Don(resqcapt19)