iwire
9 recept. circuits is 12 current carrying conductors as you forgot the 3 neutrals as well as the 9 ungrounded conductors.
10-20 conductors means your derate factor is 50%or 15 amps. You need to add another conduit. 240.4(D) #10 30 amps.