Using "test taking" logic I would go for 35a since it is the only one that is divisible by 7. [Linked Image]

440.22(A)"..."a protective device having a rating or setting not exceeding 175 <seven quarters> percent of the motor-compressor rated-load current..."

I bet there was a 5hp motor in there somewhere. (20aFLA)


Greg Fretwell