George, as much as I respect your input, I must disagree. According to your response that would mean every service change that I have ever done that didnt need a riser was illegal, and out of the bottom of every meter can, if it wasnt in conduit, was illegal.

According to 230.50 they shall be protected against physical damage as in (A) Service cables, WHERE SUBJECT TO PHYSICAL DAMAGE, shall be protected by any of the following.....and so on.

At this point, the electrician should know where or where not the cable itself is subject to physical damage.

Let me edit this...on the side of a house, it is not exposed to PHYSICAL DAMAGE, in this case, it is not exposed to damage that I can see.