Kyelectric, you really have no choice but to get the additional circuit(s) to this space. It may take some inovative thinking and some improvising, but there are code issues that you can not ignor.

Read 210.11(C)(3) and its Exception as well as the applicable parts of 210.52(A),(D), and (H).

Don't forget the NFPA 72 required interconnection of the smoke alarm from this space to the others if it is not already there.