Look here too 2005 NEC: 220.14(J) Dwelling Occupancies. In one-family, two-family, and
multifamily dwellings and in guest rooms or guest suites of
hotels and motels, the outlets specified in (J)(1), (J)(2), and
(J)(3) are included in the general lighting load calculations
of 220.12. No additional load calculations shall be required
for such outlets.


(1) All general-use receptacle outlets of 20-ampere rating
or less, including receptacles connected to the circuits
in 210.11(C)(3)
(2) The receptacle outlets specified in 210.52(E) and (G)
(3) The lighting outlets specified in 210.70(A) and (B)


Joe Tedesco, NEC Consultant