Even if you have all burners on for over 3 hrs it still would not be a continuous load. The elements in electric cooking appliance turn on an off even if they are on high. That is the reason for the demand factors in table 220.55. An appliance rated at 12kw (50 amps @ 240 volts) can be connected to a 40 amp circuit.

Curt


Curt Swartz