Section 250.28 requires a main bonding jumper to be installed. Article 100 defines the main bonding jumper as the connection between the grounded conductor and the equipment grounding conductor at the service.
This tells us that this connection must be made in service equipment only, and this is usually accomplished in the main service panel or main service disconnect enclosure.