So unless the definition of a "bollard, etc." is the same definition i would find for Schedule 80 PVC, I'd had to conclude that Tesla is in violation of the NEC when running Sch.40 where "any pipe is at risk for damage."
I can not agree with you here.
If the the AHJ feels the bollards prevent the PVC from being exposed to physical damage then the PVC can be Sch. 40.
The 'definition' or determination of exposed to physical damage is entirely up to the inspector / AHJ.
I personally do not like exposed PVC at all and most times that I am forced to use it exposed I use 80.
Coming up out of the ground I use RMC, RMC is also what the local power companies require when placing a riser on their poles.