Ventilation in the underfloor area is used for the information equipment room only. The ventilation system shall be so arranged, with approved smoke detection devices, that upon the detection of fire or products of combustion in the underfloor space the circulation of air will cease.

Commentary: This requirement has been revised for the 2002 Code. The underfloor area is required to be provided with smoke detection device(s). Upon detection of smoke, the circulation of air in the underfloor area must be interrupted. The most common method of interrupting air circulation is to open the circuit that supplies power to the air circulation fan.

In addition to causing cessation of air circulation in the underfloor area, the smoke detectors may provide other fire protection functions as part of a complete building fire alarm system.