Thanks for replying guys.
mike d,
Is the 125% for OCP, VA (panel schedule/load calcs), wire sizing, all?
pdh,
How did you come up with 57.282196187 ?
stamcon,
Maybe the spec sheet is incorrect, or they do not list all available configurations.
The w/h is a Rheem Eclipse ME85-18.
If I am not allowed to post links to items we're dicussing let me know and I'll edit it out.
The product spec sheet is available in pdf on the right side of the page at the below link.
http://www.rheem.com/dealers/catalogComm_detail.asp?id=389
How would this be wired?
AB @ 1 element = 4500VA / 208V = 21.63A - 30A 2 POLE OCP
BC @ 1 element = 4500VA / 208V = 21.63A - 30A 2 POLE OCP
CA @ 1 element = 4500VA / 208V = 21.63A - 30A 2 POLE OCP
Seems like the above is Single Phase...
PH-A - in VA?
PH-B - in VA?
PH-C - in VA?
Thanks Again Guys,
--Mario
[This message has been edited by Load-n-Code (edited 01-22-2005).]