My opinion

1. yes , 680.21(a)(4) allows this only on 1 family dwellings

2. No, gfci protection is not required unless it is cord and plug connected 680.22(a)(5)

3. No, NM cable is not listed for use in a wet location and it must be a minimum #12 insulated equipment grounding conductor 680.23(F)(2)