Hey guys this is a service change. If it were a new service the poco would just set another pole I assume to keep the cable from droping over drive way.So you guys are saying that I may need to raise my SE drip loop to 20'that just seems so unnessesary.If the cable coming in is the problem why wouldn`t the poco be required to raise the cable not me raise the drip loop.By the way I`m not argueing with the inspector I`m disagreeing with him.You know when two people have different opinions on the same subject not always a bad thing if done respectfully by both people.I have respect for his job...but in this case a service done 25 yrs ago and the fact is this pole is to far away from the house and the point of attactment from poco should be raised not my weatherhead location or they should spot another pole and solve the problem.He did agree to give me temp service until I figure a fix.Meeting with engineer from poco