It is a design decision, if the generator XO is bonded to the frame you need a 4 pole switch, if the XO is not bonded you need a 3 pole switch.

You can bond it or float it in the field most times.

When GFP protection is involved 4 pole switches are on the drawings. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts