Joe,
It apears that you have changed your position on this issue. Below are a couple of posts from from another thread . Look at your response to me.

resqcapt19 Moderator posted 12-10-2003 1:49 PM
Joe,
I don't think that the correction of problems with the electrical system that occur after the installation of the system are within the scope of the NEC.

quote:
_____

(A) Covered. This Code covers the installation of electric conductors, electric equipment, signaling and communications conductors and equipment, and fiber optic cables and raceways for the following:
_____

It appears that once the installation is complete, the NEC no longer has any jurisdiction over the electrical system. Maybe that is what the panel means when they said that the NEC "doesn't cover this type of wiring".
In the first picture in this thread, it is clear that some parts of the installation were not in compliance with the NEC and should have been red tagged at the time the installation was made.
Don


Joe Tedesco Member posted 12-10-2003 03:41 PM

Don:

I agree, and in the next 2008 Cycle I think that the rule should read as follows:

quote:
_____

(A) Covered. This Code covers the installation and use of electric conductors, electric equipment, signaling and communications conductors and equipment, and fiber optic cables and raceways for the following:
_____


Don(resqcapt19)