If you ran the gec continuous to one electrode then tapped off using split bolts to each unit water service you are not splicing the electrode. The taps are really bonding jumpers to each addtional water service. You should have two supplemental rods unless you have 25 ohms or less on one. You only need # 6 to the rods.