Actually..The purpose of the bonding of all conductive parts in and around the pool is to eliminate any possible voltage gradients between any of the surfaces associated with the pool. There is no requirement that this bonding be connected to any grounding electrode or equipment grounding conductor. See 680.26(C) Common Bonding Grid