When we figure what the VA is per outlet (strap), the result is less than 180 VA. Section 220.3(B)(9) indicates that the minimum per strap is 180VA.

20 x 115 = 2300 VA 2300VA/13 = 176.9 or 177 VA per outlet, less than the required 180VA


Joe Tedesco, NEC Consultant