517 Requires a second circuit to an OR, either a second transfer switch or normal power.
We put in isolated power for the main feed to each OR(critical branch).
Do you think the second feed needs to be isolated power as well.
This has come up with ACHA in florida.
every other state we work in has allowed us to just use 2 GFI receptacles on normal power for the second circuit.