ok for the quick note for 200 amp service

yes you are required have 2 ground rods at least 8 ft long and spaced 6 foot apart and the ground wire have to be # 4 bare ( generally very common type)

most power companines generally not allow the ground wire to be attached at meter socket but the ground wire will go straght to breaker box

as for the main box the nuetual will be bonded and yes it is a mantory requirement

as far for service enternce cable what type of cable or have conduct above meter box ?? it will make a diffence depend on the area

the last thing about gfci in bathrooms yes you can use the gfci breakers it will meet nec codes but it will be inconveent when it do trip ya have to run down to breaker box to reset each time most of sparky here genrally use gfci repectale in bathroom