400.8 was revised for the 2002 code cycle to make it clear that cords are not permitted above ceilings. In the '99 code, the word "concealed" applied to the ceiling space and cords would be permitted above "lay-in tile" ceilings. The word "concealed" was replaced with "located" in the 2002 code.
Don


Don(resqcapt19)