Quote
Now, someone else can bring up the misapplication of “floating” knockout boxes.


314.23(H) Pendant Boxes.

An enclosure supported by a pendant shall comply with 314.23(H)(1) or (2).

(1) Flexible Cord. A box shall be supported from a multiconductor cord or cable in an approved manner that protects the conductors against strain, such as a strain-relief connector threaded into a box with a hub.

400.10 Pull at Joints and Terminals.

Flexible cords and cables shall be connected to devices and to fittings so that tension is not transmitted to joints or terminals.

FPN: Some methods of preventing pull on a cord from being transmitted to joints or terminals are knotting the cord, winding with tape, and fittings designed for the purpose.


Joe Tedesco, NEC Consultant