Harold,

This looks like a fun question.

1. This fixture could only be installed if there is no ceiling tile.. Don't leave out 400.8(5) & visit 410.30(C)(1)(2)

2 See 410.21 &250.118(9)

3. This would be a stretch. If the cables are not connectd, then they obviously do not supply an outlet or a switch. However, one definition of "termination" means end. Since the wires are an end of a run then you could possibly require a box. i wouldn't bet my paycheck on it though.

Tom