1. The GEC must be sized per 250.66 2. Although it must not be spliced, it may be tapped onto by the GEC from each 200 amp panel. 3. I would connect it into one panel and then run a # 4 from the 2nd panel to tap onto it. 4. The #6 GECs should also be able to just tap onto it.
Disclaimer-- as always, if there is significant costs invloved , check with AHJ first!