1000V arc + Natural Gas + O2 = KaBoom!
if memory serves, there's a fairly narrow ignition window re; gas/air ratio.....part of the article in question.....
The equipment grounding conductor for the circuit that may energize the piping shall be permitted to serve as the bonding means.
HB commentary......
Section 250.104(B) was revised for the 2002 Code to state that gas piping is treated exactly the same as all "other metal piping" systems within a building.
so...is the confusion the EGC's possible inability to 'bond' an interior mettalic gas pipe which, thru the gas unit's structure isolated from said EGC ???