I'm just asking Joe if I'm interpretting his comment correctly.


1. Metal studs ARE NOT structural steel.(I mean I don't think you can stretch NFPA 780 to include a metal stud)
Thus there is no specific code requirement to bond them - ...even IF they could become energized (!)

I'm looking around this section of the code and can't find anything specific [would welcome 'a point in the right direction to find a specific code requirement if there is one]....and I think that's why you are suggesting someone send in a proposal 'on that issue'.
i.e. 'IF these metal studs are subject to becoming energized, THEN they are required to be bonded (and this 'could' accomplished by using metal boxes).

If I am understanding you correctly I agree whole-hardedly (boy it would be embarrassing to be agreeing whole-hardedly and that's not what Joe meant!).

That's the standard we use, and we require a separate equipment grounding conductor be run in all conduit and cable (now that's a proposal I'd like to see made).