Redsy,

I saw you mention going up another peak and thought maybe it could be attached there so as to be closer (shorter run) to the meter.

Here the SE cable must be protected on the outside up to 8 feet from grade. Coming out of Meter enclosure we would usually sleeve the SE inside a 2" PVC offset w/short piece of conduit and use a sillplate.

Bill