i'm really weak on generators and emergency circuits..... ok, i'm weak on everything [Linked Image] anyway, plans are showing an emergency generator serving two buildings [one existing with the e-gen. and one planned] on the same property, but it doesnt show a disconnect entering the new bldg or a transfer switch at the generator.. all it shows is a single emergency power circuit coming from the existing buildings generator.

is a transfer switch at the generator location the correct way to do this? 700.6

is it allowed to use a relay at the second building to signal the generator that the e-circuits are needed?

and i assume i would need to put phenolic labels at both buildings even if its only e-power? 225.37 for svc. 700.8 for gen.

225.31 says it needs a disconnect regardless of their being emergency circuits or normal? and to be s.u.s.e. 225.36

anything else?