16amps is the correct design load for a 20amp circuit.

20amps is a lot of continous power for a residence. At 10amps and 120v you can go 150 ft before a 5% voltage drop on the same circuit.

I like to run 50amp 240v to subpanels and then feed 20amp circuits from those. It solves the voltage drop problem.