I would treat the t-stat like any other switch. See 380-14(a). The 22Amp t-stat is good for the 18.75Amp load. The wiring is sized no more than 80% so there will not be any heat buildup at the terminal screws, and there is no service factor, like in motors, to worry about with the resistive load.