Mike,
Only the disconnect is required to break both conductors. A thermostat is not required to break both sides of the line. If the thermostat has the word "off" on it, then it is a combination thermostat and disconenct and must then break all hot conductors.
See 424-20.
Don(resqcapt19)


Don(resqcapt19)