hi,
does a 1-1/4" EMT stubbed up through the concrete slab into a detached garage have to be bonded?" by the way it was also installed outside the wall"
i was thinking that i would need an emt connector and a bushing on the exterior side and have to set a box on the inside in order to bond the conduit via the EGC in the 10-2 W/G.
i thought it may be easier to just use 1/2" pvc, LB stubbed into the wall and abandon the stubbed up EMT...
i beleive article 250.86 EX 2 releives me of grounding the sleeve.
thanks for any thoughts...
-regards
frodo