The situation you'd run into with the 208V to Neutral would be that standard 1 pole C/B's would not be rated for the voltage, as they're rated at 120V
If you were to use a C/B with a higher rating (277V), or use a fuse with a 250V rating, then I don't think that there's anything to prohibit it in the Code.