Although a shunt-trip breaker is an acceptable method, the circuits can be run through electrically held contactors controlled by the fire panel. The benefits are that you don't have to lose the extra breaker space required by the shunt c/b, no external power is required to operate the shunt in the event of the shunt's control circuit being turned off (which could go undetected), and $$$.