Most generators I've seen have an integral circuit breaker. I'll give the following example. A 50KW 120/208V. 3 phase 4/W. The generator would be the only power source to feed a panelboard 50 feet away that will be used in a Park setting for a special event. I would ground and bond at the generator and isolate the neutral in the "remote" panelboard. My feeder assembly would consist of (three) phase conductors, a neutral conductor and an equipment grounding conductor. Does anybody disagree with this installation?