Bosco,

It couldn't hurt labeling it in the panel. I don't know of any code rules requiring it though. It probably is not considered much of a concern as the ratings are close and if you look at Table 310-16 14awg wire (at 60C) has an allowable ampacity of 20 amps anyway - you just aren't supposed to use it as such.

Bill


Bill