Originally posted by cinkerf:
Bill, I agree with you. Adjacent areas that are "unfinished in basement" and receptacles are requested by customer should be of the GFCI type.
What I mean is that in the "Finished" room I like to put GFCI protection if it is adjacent to an unfinished area (especially if it is being used as a play area). I feel if the area adjacent is unfinished it is very likely that the receptacles in the finished room may be used as power in the unfinished area via an extension cord. But I am careful not to include the lighting downstream from the GFCI. (I know this is not required)