The same is true of transformers- the delta primary in a delta/wye tends to trap circulating current, and thus must also be rated (or derated) to handle the harmonic current.

Rated mean K-Factor rated correct? Either use a K-Factor rated transformer or derate in kva to make sure that the the rated-temperature rise stays within limits.


Luke Clarke
Electrical Planner for TVA.